Hickory max encoder input speed

All things ecat Hickory CNC controller

Moderator: cnckeith

Post Reply
spikee
Posts: 129
Joined: Thu Feb 01, 2024 5:34 am
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Contact:

Hickory max encoder input speed

Post by spikee »

Hi, I was just thinking about adding scales to the hickory... cause why not :mrgreen:

One thing I noticed in the Manual is that the Hickory supports up to 1.2MHz input speed on the encoder input.
Which is not bad, but considering if you rapid at 50-60m/min , that limits your resolution of the scales.

What I noticed in the Oak datasheet is that it allows you to go up to 6MHz, after changing a parameter bit. Considering the Hickory is presumably an evaluation upon the Oak I would almost imagine that the same trick can be done for the hickory. is that true?


eng199
Posts: 447
Joined: Fri Jan 10, 2014 11:29 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Howard, PA

Re: Hickory max encoder input speed

Post by eng199 »

Typically encoders will not output over 1MHz. Often they are 300kHz to 500kHz maximum.
Scales or encoders that are high resolution and high speed will typically use a serial protocol rather than A/B quadrature.

It is unlikely that the 1.2MHz limit is an issue.

If you really intend to use scales that support unusually high frequency, we can double check the functionality of P323 high speed filters with HICKORY. The feature does appear to be implemented, but it needs a re-test because it was not intended to be used.


spikee
Posts: 129
Joined: Thu Feb 01, 2024 5:34 am
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Contact:

Re: Hickory max encoder input speed

Post by spikee »

Hi, unless i missed something the hickory does not support serial protocol encoders?

I will have a think about what kind of resolution i want for the encoders and if that fits the 1.2mhz limit.


eng199
Posts: 447
Joined: Fri Jan 10, 2014 11:29 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Howard, PA

Re: Hickory max encoder input speed

Post by eng199 »

The 3 DE9 connectors on HICKORY do not support serial protocols. At some point, an encoder expansion board will be released. It has BiSS support.


spikee
Posts: 129
Joined: Thu Feb 01, 2024 5:34 am
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Contact:

Re: Hickory max encoder input speed

Post by spikee »

Thank you for the feedback. I will keep it in mind :)


juspk
Posts: 17
Joined: Thu Aug 15, 2024 11:02 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Hickory max encoder input speed

Post by juspk »

eng199 wrote: Wed Jun 12, 2024 10:41 am Typically encoders will not output over 1MHz. Often they are 300kHz to 500kHz maximum.
Scales or encoders that are high resolution and high speed will typically use a serial protocol rather than A/B quadrature.

It is unlikely that the 1.2MHz limit is an issue.

If you really intend to use scales that support unusually high frequency, we can double check the functionality of P323 high speed filters with HICKORY. The feature does appear to be implemented, but it needs a re-test because it was not intended to be used.
I'm in the process of a Hickory build and I have a programmable encoder for my spindle. My spindle will max out at 8000 rpm. With the Hickory limited to 1200 KHz does that means I'm limited to 9000 PPR? While I understand that is definitely enough resolution, it would be nice to use more since I have it available. My question is, did P323 ever get implemented on the Hickory like it is on the Oak controller?


eng199
Posts: 447
Joined: Fri Jan 10, 2014 11:29 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Howard, PA

Re: Hickory max encoder input speed

Post by eng199 »

Even if your encoder supports that rate, I can think of no reason to do it.
The index pulse is a critical signal for the spindle encoder and you will be making it incredibly short. The better option is to keep the line frequency below 1.2MHz and make sure P323 is set to 127. This improves noise immunity, while the alternative is unlikely to improve anything. Running multi MHz signals through a noisy environment should be avoided, which is why very few encoder manufacturers provide those rates.

The purpose of the high frequency input was to allow 3rd party drives to run high rates into MPU11 systems for velocity mode. Those systems typically had a cable 5 or less feet in length from the drive's encoder repeat. The feature was not intended for scales or spindles with long cables leaving the cabinet.


cncsnw
Community Expert
Posts: 4619
Joined: Wed Mar 24, 2010 5:48 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No

Re: Hickory max encoder input speed

Post by cncsnw »

eng199 wrote:make sure P323 is set to 127
Am I missing something here?

The operator's manual says that P323 is a bitmap by axis number.

Therefore, P323=127 would be selecting the low-speed filter for axes #1 through #7.

However, prevailing practice on Hickory systems seems to be to assign the spindle encoder as axis #8.

Wouldn't that require P323 = 255 (or at least, P323 = 128) to apply the low-speed filter to the spindle encoder as axis #8?


eng199
Posts: 447
Joined: Fri Jan 10, 2014 11:29 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Howard, PA

Re: Hickory max encoder input speed

Post by eng199 »

Thanks for pointing that out. I'll get the manual fixed.

P323 bits 5..0 correspond to MPU11 encoder plugs 6..1. Bit 6 is the MPG. This is the hardware level numbering, which differs from P308-315, where the MPG is 15.

I did notice that P323 has no effect on MPU13/HICKORY. The filters are implemented, but there is no pathway for the parameter value to get to the filter module.


Post Reply