New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

Gary Campbell
Posts: 2359
Joined: Sat Nov 18, 2017 2:32 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: Acorn 238
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Bergland, MI, USA
Contact:

Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn

Post by Gary Campbell »

You need three normally open contacts in your estop contactor.
1 breaks the VFD Common
1 breaks power to your IPC-5
1 closes the NO Fault input to C86ACCP
My version is similar but has a couple differences:
1) If the VFD is 230vac (1ph), then both hot legs should be broken by the contactor
2) If the IPC-5 is run on 115vac (I prefer 230vac), then 1 set of contacts will work fine, if not see (1) above and use a smaller separate contactor
3) There is no logical reason to break power to the C86ACCP during an estop. I prefer to power it from the 2nd set of power terminals on the Acorn board. Acorn is powered up, C86ACCP is powered up.
GCnC Control
CNC Control & Retrofits
CNC Depot Modular ATC kits
https://www.youtube.com/user/Islaww1/videos


martyscncgarage
Community Expert
Posts: 9958
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: Yes
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Mesa, AZ

Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn

Post by martyscncgarage »

Gary Campbell wrote: Sun Apr 30, 2023 8:28 am
You need three normally open contacts in your estop contactor.
1 breaks the VFD Common
1 breaks power to your IPC-5
1 closes the NO Fault input to C86ACCP
My version is similar but has a couple differences:
1) If the VFD is 230vac (1ph), then both hot legs should be broken by the contactor
2) If the IPC-5 is run on 115vac (I prefer 230vac), then 1 set of contacts will work fine, if not see (1) above and use a smaller separate contactor
3) There is no logical reason to break power to the C86ACCP during an estop. I prefer to power it from the 2nd set of power terminals on the Acorn board. Acorn is powered up, C86ACCP is powered up.
There is a no fault input that needs to be shorted on C86ACCP. On contact on the Estop relay dies that

I do not power down VFDs. They take too long to boot up, I open the COM control wire which commands the FWD/REV motor direction. Centroid has been controlling VFDs that way forever.

Agree, if the device is 220/240VAC or three phase, ALL hot legs must be broken.

There are many ways to do things, but it's best if the users follow the Centroid schematics.

Gary, is there not a Centroid Schematic for Teknic servos/IPC-5, VFD, Estop Circuit with contactor??

I'm not home, can't easily look it up

Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


Gary Campbell
Posts: 2359
Joined: Sat Nov 18, 2017 2:32 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: Acorn 238
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Bergland, MI, USA
Contact:

Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn

Post by Gary Campbell »

There is a no fault input that needs to be shorted on C86ACCP. On contact on the Estop relay dies that
Yes there is. It comes shorted from CNC4PC.

I'm sure they (Centroid) have schematics, but I have chosen to simplify the wiring on my builds because adding that portion complicates the process and serves no purpose or gain
GCnC Control
CNC Control & Retrofits
CNC Depot Modular ATC kits
https://www.youtube.com/user/Islaww1/videos


martyscncgarage
Community Expert
Posts: 9958
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: Yes
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Mesa, AZ

Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn

Post by martyscncgarage »

Gary Campbell wrote: Sun Apr 30, 2023 10:01 am
There is a no fault input that needs to be shorted on C86ACCP. On contact on the Estop relay dies that
Yes there is. It comes shorted from CNC4PC.

I'm sure they (Centroid) have schematics, but I have chosen to simplify the wiring on my builds because adding that portion complicates the process and serves no purpose or gain
My question about schematics was for the fellow looking for help.
Thanks Gary
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


Gary Campbell
Posts: 2359
Joined: Sat Nov 18, 2017 2:32 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: Acorn 238
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Bergland, MI, USA
Contact:

Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn

Post by Gary Campbell »

My question about schematics was for the fellow looking for help
Yes. same here. I was trying to simplify his build
GCnC Control
CNC Control & Retrofits
CNC Depot Modular ATC kits
https://www.youtube.com/user/Islaww1/videos


ShawnM
Community Expert
Posts: 3041
Joined: Fri May 24, 2019 8:34 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804734C6498-0401191832
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Clearwater, FL

Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn

Post by ShawnM »

Gary Campbell wrote: Sun Apr 30, 2023 10:28 am ........ I was trying to simplify his build
Too late Gary, he already bought the C86ACCP. :lol:


Gary Campbell
Posts: 2359
Joined: Sat Nov 18, 2017 2:32 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: Acorn 238
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Bergland, MI, USA
Contact:

Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn

Post by Gary Campbell »

Too late Gary, he already bought the C86ACCP. :lol:
That's comedy 😁. I understand that some components are a bit complicated for some folks.

I know they make the motor connections easier for my customers and give them the option to use properly cut to length landed wires in the terminals or plug directly into the minifit jr connectors
GCnC Control
CNC Control & Retrofits
CNC Depot Modular ATC kits
https://www.youtube.com/user/Islaww1/videos


Post Reply