Huanyang VFD issue

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

Post Reply
Swarfmonger
Posts: 4
Joined: Fri Feb 22, 2019 3:49 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 74E1828900E1-1019181259
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Huanyang VFD issue

Post by Swarfmonger »

Hello,

I have been retrofitting a vertical mill with an Acorn board and am down to my last couple of installation issues and would really appreciate some help on one of them. I am using a Huanyang VFD (HYD1D523B) and it has been wired using your Rev 3 schematic with the exception of placing the common wire in the FC position instead of the FA since I read somewhere on this forum that the print was not correct in that regard. The motor specs are: 220V,1720 RPM,6.5 amps,60 cycles.

Everything seems to be working as it should with the exception of the speed control. the pot on the VFD will alter the speed fine but the Acorn board will not alter it at all. I have already inspected the 0-10V output on the Acorn board and it seems to be working as it should (10 volts at full power,5 volts at half power Etc.) but the speed remains constant when I try to change it with the controller. I think it might be a programming issue in the VFD itself based on the evidence but I can't say for sure. I am new to this so if I am not explaining the situation clearly or have given inadequate information,please accept my apology in advance.

Regards,
Dave
Attachments
report_74E1828900E1-1019181259_2019-02-22_11-58-14.zip
(183.23 KiB) Downloaded 131 times


Gary Campbell
Posts: 2363
Joined: Sat Nov 18, 2017 2:32 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: Acorn 238
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Bergland, MI, USA
Contact:

Re: Huanyang VFD issue

Post by Gary Campbell »

If the speed works from the panel potentiometer, then you must set the frequency control method parameter to "0-10v" instead of the pot.
GCnC Control
CNC Control & Retrofits
CNC Depot Modular ATC kits
https://www.youtube.com/user/Islaww1/videos


bmilam
Posts: 152
Joined: Sun Sep 16, 2018 7:51 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Huanyang VFD issue

Post by bmilam »

Look at your manual and see if there is a jumper setting for it. On mine, to the right of where the wires go, there are 3 small pins with a jumper. I had the same problem with mine and it took me a while to finally figure out that the jumper was wrong. It should be one of the first things inside your manual in the set up. It is very easy to overlook because they are small.


martyscncgarage
Community Expert
Posts: 9958
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: Yes
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Mesa, AZ

Re: Huanyang VFD issue

Post by martyscncgarage »

How close are you to these attached sheets?
Also, you can benchtest your VFD before connecting to Acorn.

See this for benchtesting a VFD: viewtopic.php?f=61&t=2446

Marty
Attachments
HuanYuang HY Series VFD Setup for 0-10v input 180529.pdf
(18.28 KiB) Downloaded 145 times
Huan Yang HY Series Revised Schematic 180529.pdf
(402.55 KiB) Downloaded 141 times
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


Ken Rychlik
Posts: 579
Joined: Wed Jan 23, 2019 4:19 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 80F5B5B92C3A-0213236854
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Huanyang VFD issue

Post by Ken Rychlik »

If the manual speed dial is working on the vfd, you do not have the vfd param settings done right.
Ken


cncman172
Posts: 254
Joined: Thu Nov 02, 2017 4:07 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 985DAD429EE9-0926170118
DC3IOB: No
CNC11: No
CPU10 or CPU7: No
Location: Westerville, Ohio

Re: Huanyang VFD issue

Post by cncman172 »

These type of VFD's work perfect with Acorn. You have to change a couple of parameters in the VFD to tell it you are getting the Speed from the analog inputs and you have to tell it you are controller from an external sources for FWD and REVERSE. I have this same VFD on my system with the Acorn and it works perfect. On key hint is make sure you use heavier gauge wire for the analog inputs or they will bounce and change speeds constantly. I used a pair of 18 AWG wires and it works perfect. If you go with like 22 or 20 AWG and you see the spindle speed changing that is your issue.

If you can't figure out the parameters let me know and I will post them.

Russ


Swarfmonger
Posts: 4
Joined: Fri Feb 22, 2019 3:49 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 74E1828900E1-1019181259
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Huanyang VFD issue

Post by Swarfmonger »

Thanks for all of the replies,I really appreciate it! As it turns out bmilam hit the nail on the head. Once the jumper was set to the proper location for remote speed control use it sprung to life and started behaving exactly as it is supposed to. Thanks again to everyone taking the time to help,This is a great product and this forum makes it that much more great.

Regards,
Dave


bmilam
Posts: 152
Joined: Sun Sep 16, 2018 7:51 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Huanyang VFD issue

Post by bmilam »

Glad it worked for you. It took me a few days to trace down the same issue on mine.


Post Reply