default parameters

Posted: Wed Nov 23, 2011 12:29 am
by chris.poirier
While bench checking my DC3IOB/MPU11 I found that drive fault 1 and 2 do not have continuity when I jump the e-stop input. I think I may have fat fingered a parameter when doing the checkout as on initial start up I could hear relays click. Now when I recycle the power I do not hear a thing. Is there an easy way to reset the parameters rather than check 1 by 1 with the list in the manual, or can some one help me narrow this down? everything is preped and ready to go together. Only took me a year............ :D

Chris

Re: default parameters

Posted: Thu Dec 01, 2011 7:04 am
by Maint_1
Have you done a report from the utility menu before changing parameters? If so you could restore to original from that.

Re: default parameters

Posted: Mon Dec 05, 2011 2:02 pm
by chris.poirier
I got some help from Ajax and found my real problem was I had fiber 5 in 5 on the DC3IOB and not in MPU115.
Bench tested OK and will be installing this week after work. :D

Chris