hurco hawk 5 retrofit
Re: hurco hawk 5 retrofit
What "touch" computer do you have? Where did you acquire it? Picture?
Sounds hardware or Windows driver related perhaps.
Its not an All in One PC with touch screen is it? I personally do not like those. Something happens with either the monitor or the PC and you have to replace the whole thing.
I like resistive touch screens. Guys have been having good success with these Viewsonic monitors:
https://www.amazon.com/dp/B01M1PA4DQ/re ... LEbX36Y1GE
jtroedel8487
Post by jtroedel8487 »
Marty the computer is an Inspiron 23 all in one model 5348. I’ve been playing around a little bit with it and have found that if I have power off to servo drives and spindle vfd the problem goes away. Works flawlessly. When drives are on and communicating with the computer I get the freezing issue. Leads me to believe it could either be a voltage issue or emi.
jtroedel8487 wrote: Thu Apr 16, 2020 10:12 am Marty the computer is an Inspiron 23 all in one model 5348. I’ve been playing around a little bit with it and have found that if I have power off to servo drives and spindle vfd the problem goes away. Works flawlessly. When drives are on and communicating with the computer I get the freezing issue. Leads me to believe it could either be a voltage issue or emi.
Can you post a report, F7 Utilities, F7 create report.
Or look at your Error log and see if you have RESENDS
You are using the shielded Ethernet cable that came with Acorn, from the PC to Acorn correct?
jtroedel8487
Here are some pictures of the computer and ethernet cable hooked to acorn. I am using the shielded cable provided by centroid. Also here is the report.
report_780473A91E45-0919192474_2020-04-01_06-52-43.zip
(269.59 KiB) Downloaded 107 times
jtroedel8487
found the error log you were talking about also. here's a picture of the log file screen. getting a 9033 fault. looked it up and says it could be related to a corrupt plc file?
Press F3 PREVIOUS Page.
On and before 3/30/20 You had multiple resends. So you had some noise issues:
Have those been resolved?
(4) 03-28-2020 19:41:53 944 MPU requested resend # 14
(4) 03-28-2020 19:41:53 946 PC resending # 742
(1) 03-28-2020 19:41:55 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-28-2020 19:41:56 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 19:41:56 944 MPU requested resend # 17
(4) 03-28-2020 19:41:56 946 PC resending # 814
(4) 03-28-2020 19:42:01 4032 Reset Cleared
(4) 03-28-2020 19:42:09 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 19:42:17 4032 Reset Cleared
(4) 03-28-2020 19:42:21 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 19:42:24 4032 Reset Cleared
(4) 03-28-2020 19:42:36 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 19:42:40 4032 Reset Cleared
(1) 03-28-2020 19:42:47 406 Emergency stop detected
(1) 03-28-2020 19:42:53 406 Emergency stop detected
(4) 03-28-2020 19:44:46 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 19:45:04 4032 Reset Cleared
(4) 03-28-2020 19:45:06 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 19:45:08 4032 Reset Cleared
(4) 03-28-2020 19:45:19 944 MPU requested resend # 18
(4) 03-28-2020 19:45:19 946 PC resending # 834
(1) 03-28-2020 19:47:31 204 Exiting CNC...Normal Exit (66)
(1) 03-28-2020 19:47:43 199 CNC Started
(4) 03-28-2020 19:47:48 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 03-28-2020 19:47:48 944 MPU requested resend # 18
(4) 03-28-2020 19:47:48 946 PC resending # 860
(1) 03-28-2020 19:47:49 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-28-2020 19:47:49 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 03-28-2020 19:47:49 944 MPU requested resend # 20
(4) 03-28-2020 19:47:49 946 PC resending # 919
(4) 03-28-2020 19:47:53 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 19:47:55 4032 Reset Cleared
(4) 03-28-2020 19:48:02 944 MPU requested resend # 21
(4) 03-28-2020 19:48:02 946 PC resending # 922
(4) 03-28-2020 19:48:04 944 MPU requested resend # 22
(4) 03-28-2020 19:48:04 946 PC resending # 925
(4) 03-28-2020 19:48:04 944 MPU requested resend # 23
(4) 03-28-2020 19:48:04 946 PC resending # 935
(1) 03-28-2020 19:53:05 204 Exiting CNC...Normal Exit (66)
(1) 03-28-2020 19:53:39 199 CNC Started
(4) 03-28-2020 19:53:43 944 MPU requested resend # 13
(4) 03-28-2020 19:53:43 946 PC resending # 666
(1) 03-28-2020 19:53:45 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-28-2020 19:53:46 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 19:53:46 944 MPU requested resend # 14
(4) 03-28-2020 19:53:46 946 PC resending # 722
(4) 03-28-2020 19:53:51 4032 Reset Cleared
(1) 03-28-2020 19:54:09 313 Waiting for dwell time (M26)
(4) 03-28-2020 19:54:18 944 MPU requested resend # 15
(4) 03-28-2020 19:54:18 946 PC resending # 725
(4) 03-28-2020 19:54:19 944 MPU requested resend # 16
(4) 03-28-2020 19:54:19 946 PC resending # 728
(4) 03-28-2020 19:54:28 944 MPU requested resend # 17
(4) 03-28-2020 19:54:28 946 PC resending # 731
(1) 03-28-2020 20:00:55 204 Exiting CNC...Normal Exit (66)
(1) 03-28-2020 20:01:34 199 CNC Started
(4) 03-28-2020 20:01:39 944 MPU requested resend # 14
(4) 03-28-2020 20:01:39 946 PC resending # 714
(1) 03-28-2020 20:01:41 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-28-2020 20:01:42 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 20:01:42 944 MPU requested resend # 16
(4) 03-28-2020 20:01:42 946 PC resending # 791
(4) 03-28-2020 20:01:46 4032 Reset Cleared
(4) 03-28-2020 20:02:15 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 20:02:23 4032 Reset Cleared
(4) 03-28-2020 20:04:26 944 MPU requested resend # 17
(4) 03-28-2020 20:04:26 946 PC resending # 794
(4) 03-28-2020 20:04:33 9033 Reset Initiated, Press Reset to Clear
(1) 03-28-2020 20:05:22 204 Exiting CNC...Normal Exit (66)
(1) 03-28-2020 20:05:55 199 CNC Started
(1) 03-28-2020 20:06:01 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-28-2020 20:06:02 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 20:06:11 4032 Reset Cleared
(1) 03-28-2020 20:06:32 9031 DRIVE FAULT!
(4) 03-28-2020 20:06:45 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 20:06:47 4032 Reset Cleared
(4) 03-28-2020 20:06:49 9031 DRIVE FAULT!
(4) 03-28-2020 20:07:05 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 20:07:07 4032 Reset Cleared
(1) 03-28-2020 20:08:49 406 Emergency stop detected
(1) 03-28-2020 20:09:31 204 Exiting CNC...Normal Exit (66)
(1) 03-28-2020 20:10:06 199 CNC Started
(1) 03-28-2020 20:12:45 199 CNC Started
(1) 03-28-2020 20:14:53 199 CNC Started
(1) 03-28-2020 20:17:19 199 CNC Started
(1) 03-28-2020 20:17:25 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(1) 03-28-2020 20:17:26 406 Emergency stop detected
(1) 03-28-2020 20:22:16 406 Emergency stop detected
(1) 03-28-2020 20:22:38 406 Emergency stop detected
(1) 03-28-2020 20:22:58 406 Emergency stop detected
(1) 03-28-2020 20:27:17 302 Moving...
(1) 03-28-2020 20:27:18 309 Waiting for CYCLE START button
(4) 03-28-2020 20:27:22 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 20:27:24 4032 Reset Cleared
(4) 03-28-2020 20:28:03 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 20:28:04 4032 Reset Cleared
(1) 03-28-2020 20:30:46 199 CNC Started
(1) 03-28-2020 20:30:52 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-28-2020 20:30:53 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 20:30:57 4032 Reset Cleared
(4) 03-28-2020 20:31:30 9033 Reset Initiated, Press Reset to Clear
(1) 03-28-2020 20:32:18 204 Exiting CNC...Normal Exit (66)
(1) 03-28-2020 20:43:22 199 CNC Started
(1) 03-28-2020 20:44:31 199 CNC Started
(1) 03-28-2020 20:46:11 199 CNC Started
(1) 03-28-2020 20:46:17 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-28-2020 20:46:18 9033 Reset Initiated, Press Reset to Clear
(4) 03-28-2020 20:46:24 4032 Reset Cleared
(4) 03-28-2020 20:47:40 9033 Reset Initiated, Press Reset to Clear
(1) 03-28-2020 20:47:50 204 Exiting CNC...Normal Exit (66)
(1) 03-30-2020 13:01:42 199 CNC Started
(4) 03-30-2020 13:01:47 944 MPU requested resend # 25
(4) 03-30-2020 13:01:47 946 PC resending # 1182
(1) 03-30-2020 13:01:48 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-30-2020 13:01:49 9033 Reset Initiated, Press Reset to Clear
(4) 03-30-2020 13:01:55 4032 Reset Cleared
(1) 03-30-2020 15:09:00 199 CNC Started
(1) 03-30-2020 15:11:49 199 CNC Started
(1) 03-30-2020 15:11:55 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-30-2020 15:11:56 9033 Reset Initiated, Press Reset to Clear
(4) 03-30-2020 15:12:33 4032 Reset Cleared
(1) 03-30-2020 15:15:08 204 Exiting CNC...Normal Exit (66)
(1) 03-30-2020 15:15:10 199 CNC Started
(4) 03-30-2020 15:15:14 9039 Software Exited, Cycle E-Stop/Reset to Continue
(1) 03-30-2020 15:15:16 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-30-2020 15:15:16 9039 Software Exited, Cycle E-Stop/Reset to Continue
(1) 03-30-2020 15:15:40 204 Exiting CNC...Normal Exit (66)
(1) 03-30-2020 15:17:08 199 CNC Started
(1) 03-30-2020 15:17:14 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-30-2020 15:17:15 9033 Reset Initiated, Press Reset to Clear
(4) 03-30-2020 15:17:18 4032 Reset Cleared
(1) 03-30-2020 15:29:59 204 Exiting CNC...Normal Exit (66)
(1) 03-30-2020 16:35:37 199 CNC Started
(4) 03-30-2020 16:35:42 944 MPU requested resend # 21
(4) 03-30-2020 16:35:42 946 PC resending # 958
(1) 03-30-2020 16:35:44 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-30-2020 16:35:45 9033 Reset Initiated, Press Reset to Clear
(4) 03-30-2020 16:35:45 944 MPU requested resend # 22
(4) 03-30-2020 16:35:45 946 PC resending # 998
(4) 03-30-2020 16:35:54 4032 Reset Cleared
(1) 03-30-2020 16:55:32 199 CNC Started
(1) 03-30-2020 16:55:39 (READ) Error loading WCS information!
(1) 03-30-2020 16:55:41 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-30-2020 16:55:42 9033 Reset Initiated, Press Reset to Clear
(4) 03-30-2020 16:55:51 4032 Reset Cleared
(1) 03-30-2020 16:56:29 204 Exiting CNC...Normal Exit (66)
(1) 03-30-2020 16:56:30 199 CNC Started
(4) 03-30-2020 16:56:34 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 03-30-2020 16:56:35 9039 Software Exited, Cycle E-Stop/Reset to Continue
(1) 03-30-2020 16:56:47 PLC Program change detected.
(1) 03-30-2020 16:56:49 204 Exiting CNC...Normal Exit (66)
(1) 03-30-2020 16:58:13 199 CNC Started
(1) 03-30-2020 16:58:19 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-30-2020 16:58:20 9033 Reset Initiated, Press Reset to Clear
(1) 03-30-2020 16:58:23 9030 SPINDLE FAULT!
(4) 03-30-2020 16:58:29 9033 Reset Initiated, Press Reset to Clear
(4) 03-30-2020 16:58:53 9030 SPINDLE FAULT!
(4) 03-30-2020 16:59:05 9033 Reset Initiated, Press Reset to Clear
(4) 03-30-2020 16:59:08 9030 SPINDLE FAULT!
(4) 03-30-2020 17:00:02 9033 Reset Initiated, Press Reset to Clear
(4) 03-30-2020 17:00:08 9030 SPINDLE FAULT!
(1) 03-30-2020 17:00:12 406 Emergency stop detected
(4) 03-30-2020 17:00:14 9030 SPINDLE FAULT!
(1) 03-30-2020 17:00:16 406 Emergency stop detected
(4) 03-30-2020 17:00:18 9030 SPINDLE FAULT!
(1) 03-30-2020 17:01:32 204 Exiting CNC...Normal Exit (66)
(1) 03-30-2020 17:29:50 199 CNC Started
(1) 03-30-2020 17:32:02 199 CNC Started
(1) 03-30-2020 17:32:08 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-30-2020 17:32:09 9033 Reset Initiated, Press Reset to Clear
(4) 03-30-2020 17:32:44 4032 Reset Cleared
(4) 03-30-2020 17:34:24 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-30-2020 17:35:52 9033 Reset Initiated, Press Reset to Clear
(4) 03-30-2020 17:35:55 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-30-2020 17:35:55 4032 Reset Cleared
(1) 03-30-2020 17:36:06 204 Exiting CNC...Normal Exit (66)
(1) 03-30-2020 18:12:39 199 CNC Started
(1) 03-30-2020 18:12:45 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-30-2020 18:12:46 9033 Reset Initiated, Press Reset to Clear
(4) 03-30-2020 18:12:52 4032 Reset Cleared
(4) 03-30-2020 18:12:55 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-30-2020 18:13:14 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-30-2020 18:13:33 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-30-2020 18:13:36 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-30-2020 18:14:26 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-30-2020 18:14:50 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(1) 03-30-2020 18:39:24 204 Exiting CNC...Normal Exit (66)
(1) 03-31-2020 16:32:40 199 CNC Started
(1) 03-31-2020 16:34:54 199 CNC Started
(1) 03-31-2020 16:35:00 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-31-2020 16:35:01 9033 Reset Initiated, Press Reset to Clear
(4) 03-31-2020 16:35:06 4032 Reset Cleared
(4) 03-31-2020 16:35:34 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-31-2020 16:35:54 9033 Reset Initiated, Press Reset to Clear
(4) 03-31-2020 16:36:02 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-31-2020 16:36:03 4032 Reset Cleared
(1) 03-31-2020 16:36:22 2051 Manual Coolant Mode
(4) 03-31-2020 16:36:29 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(1) 03-31-2020 16:37:00 406 Emergency stop detected
(4) 03-31-2020 16:37:07 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(1) 03-31-2020 16:38:41 199 CNC Started
(4) 03-31-2020 16:38:45 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(1) 03-31-2020 16:38:47 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-31-2020 16:38:48 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 03-31-2020 16:38:52 9033 Reset Initiated, Press Reset to Clear
(4) 03-31-2020 16:38:54 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-31-2020 16:38:54 4032 Reset Cleared
(4) 03-31-2020 16:39:12 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-31-2020 16:39:22 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-31-2020 16:39:30 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-31-2020 16:39:41 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(1) 03-31-2020 16:39:59 406 Emergency stop detected
(4) 03-31-2020 16:40:06 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-31-2020 16:40:15 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-31-2020 16:40:19 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(1) 03-31-2020 16:41:11 406 Emergency stop detected
(1) 03-31-2020 16:43:28 199 CNC Started
(4) 03-31-2020 16:43:32 9039 Software Exited, Cycle E-Stop/Reset to Continue
(1) 03-31-2020 16:43:33 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 03-31-2020 16:43:34 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 03-31-2020 16:43:45 9033 Reset Initiated, Press Reset to Clear
(4) 03-31-2020 16:43:47 4032 Reset Cleared
(4) 03-31-2020 16:44:21 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-31-2020 16:44:42 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 03-31-2020 17:01:01 9033 Reset Initiated, Press Reset to Clear
(4) 03-31-2020 17:01:01 4032 Reset Cleared
(1) 04-01-2020 6:40:23 199 CNC Started
(1) 04-01-2020 6:45:45 199 CNC Started
(1) 04-01-2020 6:48:00 199 CNC Started
(1) 04-01-2020 6:48:06 CNC12 Acorn Mill v4.20 (revision 4.20.1) Jan 17 2020, 09:50:30
(4) 04-01-2020 6:48:07 9033 Reset Initiated, Press Reset to Clear
(4) 04-01-2020 6:48:15 4032 Reset Cleared
(4) 04-01-2020 6:48:37 5038 SPECIFIED SPIN SPEED < MIN SPIN SPEED
(4) 04-01-2020 6:49:29 9033 Reset Initiated, Press Reset to Clear
(4) 04-01-2020 6:49:32 4032 Reset Cleared
(4) 04-01-2020 6:50:47 9033 Reset Initiated, Press Reset to Clear
(4) 04-01-2020 6:50:48 4032 Reset Cleared
(1) 04-01-2020 6:52:43 Creating report...
Also, there are orange wires draped around cables behind the PC. What are those?
You should do some wiring house keeping.....
jtroedel8487
Those are connected to the physical estop switch. I suppose this is why you guys harp on all shielded wires 🤷🏻‍♂️ As far as the noise issues I wasn’t even aware! At least I now know what to try and correct, thanks
Yes. Resolve the requests to resend. Those are Ethernet communication errors. Make sure ALL grounds and shields go back to one point where the service ground comes in. Also, only ground ONE end of cable shield drain wires.
You have to clean up your wiring. Try NOT to use single conductor wire. For Estop, I use a 4 conductor cable. Estop button should have two NC contact blocks. That cable doesn't necessarily have to be shielded but is good practice
jtroedel8487
Good advice! I will defiantly be ordering some more wire. Not knowing what I’m doing I had cut off the drain wire inside the shielded wire that I have. Didn’t realize I was supposed to ground it. I’m sure this makes the shielding have no affect.