Spindle 24000 RPM with 2 Pulses per Revolution <Resolved>
Angelo DiCenso
CNC Control System Serial Number: cnc12 Mill Pro E0623483321F-0412225912,CNC Router Pro E0623479658B-1022203857
Post by Angelo DiCenso »
Hello All Forum Members.
I am running into an issue with a 24000 RPM spindle
The spindle sensor puts out 2 pulses per revolution for a total of 48000.
As far as I know the Acorn can only handle about 1000 (I could be wrong)
If I start the spindle, I can read the speed go up to App. 3700 RPM and then it drops to 0. A=0
I am using “INPUT2” and if the spindle stops on the two sensing spots the input will show the wrong status.
Imagine returning a tool to the carousel at about 20k RPM.
The only input I can think of that can read 48000 pulses is the Encoder Input (I could be wrong)
After reading lots of forum documents maybe this can be a fix.
Please look at this Idea and let me know if it will work, You fix, how did you do this or that I am crazy ETC.
This is the Optocoupler Isolation Board, Icstation DC 24V Optocoupler Isolation Module EL817 1 Channel Opto PNP NPN Signal Converter, Isolator High-Level Trigger 80KHz, and my hookup schematic
eng199
Re: Spindle 24000 RPM with 2 Pulses per Revolution
Post by eng199 »
Z is a differential input. I think your diagram is showing /Z tied to ground. This will be unreliable at best. A 26LS31 or equivalent driver is required to drive that input.
I'm not sure what the goal is here. Typically a spindle encoder is required for orient and orient is required for carousel tool changers.
Angelo DiCenso
Hello eng199;
I am trying to obtain a good spindle speed =0
a) The spindle RPM sensor ( INPUT2 ) does not reed if spindle speed of 0 . If the spindle stops on any of the two sensing spots the input #2 will not
register correctly. This eliminates that and RPM sensor is not reliable.
b) Memory state #4119 has the incorrect info and it will not tell the plc the correct spindle speed the spindle enters the carousel still rotating
c) The only way so far for me to assume that the spindle is at 0 RPM is adding a time delay of a minimum of 8 seconds which is needed during a job
tool change and not on a tool change where the spindle is not rotating.
d) I have looked for a way for the VFD to communicate speed = 0 but so far no luck.
Any suggestions???
centroid467
Post by centroid467 »
What inverter are you using to drive this?
Is it the TB Wood's device on the AXYZ router? If so, I would look at the linked page in the manual. I'm guessing that the relay output is used for the fault output so you would use the ST1 terminal and set the corresponding parameter to either 3 or 6. You may have to set whether the corresponding Acorn input is looking at NO or NC in the Wizard.
https://www.mikrocontroller.net/attachm ... df#page=71
Angelo DiCenso
Hello centroid467;
I am using a FULING DZB 312
centroid467
According to this manual (https://www.cncwiki.org/images/f/f9/Ful ... df#page=12) you should use the MO1 terminal to the Acorn input and the MCM terminal to the 24V power supply common ground.
Set VFD parameter F2.19 to 6 for "zero speed operation".
Angelo DiCenso
Great centroid467, should that input still be (INPUT2 RPM Sensor) ?
centroid467
No, I would set it to "VFDZeroSpeed". You may need to click the input number to set it to NO or NC depending on what the VFD outputs.
Angelo DiCenso
Thank You centroid467
I will do so and let you know the outcome.
Angelo DiCenso
Centroid467;
The output M01 is not on this VFD
There is M02 and MCM.
Since the two schematics are different what shoud be the wiring for it
