"Everybody" does not wire their control cabinets the same. What service you bring into the control cabinet depends entirely on the power requirements of the components you choose to put in your control cabinet. Some work with 120VAC single-phase. Some work with 240VAC single-phase. Some work only with 240VAC 3-phase.

I suspect you do not have a clear view of what the contactor does, and how switching AC (or DC) power works.
vwfan wrote:One leg goes to the VFD one leg goes to the C 86,and one to the icp5
Let us suppose that you are supplying 240VAC single-phase to your VFD, and 240VAC single-phase to a Teknic IPC-5 power supply. I have no idea what a "C 86" is, so you will have to explain its function or power requirements.

Since both the VFD and the IPC-5 receive the same type of power, and both should have their power disconnected when the E-stop contactor is open, you can use two of the three poles of the contactor to switch the two legs of your 240VAC single-phase supply: two legs in, two legs out. The two outgoing legs would then be wired in parallel to both the VFD and the IPC-5.

That would leave one pole unused.

If the "C 86" uses 240VAC single-phase power, then it could just be wired in parallel with the VFD and the IPC-5, and you would not need the third pole of the contactor at all. If the "C 86" uses 120VAC single-phase power, or some low-voltage DC power, and that power needs to be switched with emergency stop, then you could wire that power through the third pole of the contactor. Alternately, if the "C 86" requires some sort of low-voltage DC logic signal that tells it when the contactor is closed, that too could be wired through the third pole of the contactor.


Upnorth
Posts: 239
Joined: Wed Apr 01, 2020 8:23 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 1702
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Which contactor and snubber

Post by Upnorth »

Vwfan wrote: Wed Jul 13, 2022 1:52 pm Yes basically everything you just explained I already know I’m asking because all the videos and everything everybody says the E stop contactor is 3 phase , it has three ins and three outs! If I need to power three things on the output side,how do I get 3 lines out of the contactor with only having 2 lines going in to it? Or do I split one of the 2 220 and make it so there are 3 going to input on contactor ?
It's sort of difficult to answer your questions. Every box is wired differently. It depends on what you have available and what you need it to do. If you lived close to here I would say bring the box over and tell me what you need it to do. Then it could be set up as required. I tend to bring in all power through a switch and breaker to the DIN rail. From there I split it up to do whatever I need. Some busses are switched, some are not. Some are part f the E-stop.

Might be best if you draw schematics of what is available and what you need to do. Written information is hard to understand and answer questions on. A schematic can be corrected and is easier to understand.


Vwfan
Posts: 201
Joined: Tue Dec 21, 2021 1:59 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Which contactor and snubber

Post by Vwfan »

OK awesome I definitely appreciate both your guys help I am in metro Detroit Michigan I’m not really sure where you’re located, I am almost 39 years old now and it’s just now starting to sink in that it’s very difficult for me to learn things without doing them with my hands, so I think once I get this cabinet wired completed I should really have a better understanding of how it all works. Believe me I’m daily reading through all this schematics all these posts all the Facebook and YouTube videos just trying to beat it into my head so I can wrap my house head around it. By no means is this out of my ability I just get confused a little bit and really I appreciate all of your help more to come thank you


cnckeith
Site Admin
Posts: 9075
Joined: Wed Mar 03, 2010 4:23 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Contact:

Re: Which contactor and snubber

Post by cnckeith »

fyi for anyone reading this thread..related info is here.
https://centroidcncforum.com/viewtopic. ... 292#p47292
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63

Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html


Vwfan
Posts: 201
Joined: Tue Dec 21, 2021 1:59 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Which contactor and snubber

Post by Vwfan »

So I picked up a lathe over the weekend and it’s already been converted with a VFD as a very nice little control panel but it has an awesome on/off‘s contactor that the switch is on the outside of the box running a bar into the contactor inside the box I’m wondering does anybody know of any of this style that you can use and run the e stop with it also ?
Attachments
83B763A2-F546-47C9-9C26-4AC29D4A33E3.jpeg
E530102E-7442-44C1-867A-A420DE0D1B93.jpeg
2284728A-5D5D-4696-8D4E-170C095A7EA2.jpeg


ShawnM
Community Expert
Posts: 3052
Joined: Fri May 24, 2019 8:34 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804734C6498-0401191832
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Clearwater, FL

Re: Which contactor and snubber

Post by ShawnM »

That style extended rotary knob is very common on professional cnc equipment. Your e-stop needs to be in a very convenient place up top and easy to get to. Not sure where that electrical enclosure is mounted on the machine from your pics but I'd want the e-stop within an arms reach and no further. If the electrical enclosure is within EASY reach you simply drill a 22mm hole in the box and mount it in one of the sides.


tblough
Community Expert
Posts: 3557
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Re: Which contactor and snubber

Post by tblough »

That is a disconnect, not a contactor. You will need a contactor for the e-stop in addition to this.
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.


Vwfan
Posts: 201
Joined: Tue Dec 21, 2021 1:59 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Which contactor and snubber

Post by Vwfan »

That’s more so what I was after I guess I was looking to see if there was a disconnect within contactor kind of built into one but now that I understand it I may add one of these to my cabinet